|
G8MNY > TECH 17.04.19 10:20l 69 Lines 2690 Bytes #999 (0) @ WW
BID : 864_GB7CIP
Read: GUEST
Subj: 70-260V Mains Auto Transformer
Path: IW8PGT<IR2UBX<SR1BSZ<GB7CIP
Sent: 190417/0919Z @:GB7CIP.#32.GBR.EURO #:864 [Caterham Surrey GBR] $:864_GB7C
From: G8MNY@GB7CIP.#32.GBR.EURO
To : TECH@WW
By G8MNY (Updated Dec 12)
(8 Bit ASCII graphics use code page 437 or 850, Terminal Font)
This is a poor variac substitute, but made with a suitable transformer & large
wafer switch, it can provide useful mains test voltages.
Voltages shown are for simplicity of calculation only!
CIRCUIT
ÚÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÂÄÄÄo 260V
Fuse 1 On ³ ÚÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÂÄ)ÄÄÄo 240V
L Äo-oÄÄÄo\oÄÂÄÄÄÄ)ÄÄÄÄÄ)ÄÄÄÄÄÄÄÄÄÂÄÄÄÄÄ)Ä)ÄÄÄo 220V <ÄÄÄ L
(220V) ³. ³ ³ - ³ ³ ÃÄÄÄo 200V
)||.ÃÄÄÄÄÄ)ÄÄÄo <ÄÄÄÙ ³ ³ ÚÄo 180V
110V )||( 40V ³ 220 ³ ÃÄ)Äo 150V
______)||(______³ 110/20 ÃÄ)Ä)Äo 130V
³______.||( 20V ³ + <ÄÄÄÄÄÄÄÂÄ)Ä)Ä)Äo 110V
³ )||( 0V LAMP o ³ ÃÄ)Ä)Äo 90V
³ 110V )|| ÀÄÄÄÄÄÁÄÄÄÁÄÄÄÄÄÄÄÄÄ)Ä)Ä)ÄÁÄo 70V
³ ___)|| ³ ³ ÀÄÄÄo 40V
³ ³ 110 ³ ÀÄÄÄÄÄo 20V
ÀÄÄ(ÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄo <ÄÄÄo-oÄÙ
³ 20/40o Fuse 2
N ÄÄÄÄÄÄÄÄÁÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÁÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄ N
E ÄÄÂÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄ E
_³_
Here the 110/220V switching & phase reverse switching (+ or -) of the 40V
secondary is not shown. The two lower secondary voltages of 20 & 40V are
available with this complex switching.
If a good 12 position multi wafer switch is not available, then a plug board
may be more suitable.
SAFETY
To stop switch arcing or shocks on a plug board, only change voltage with the
mains OFF! The inclusion of a 20V lamp (not accessible!) is useful to remind
you!
All housing & wiring etc. should be up to mains standards & also let heat out.
The power rating of the transformer will set the max current at a voltage...
VOLTS MAX LOAD CURRENT e.g. 80W Transformer
260 Full Secondary 2A
240 1.5 x Secondary 3A
220 Infinite Fuse Limit
200 1.5 x Secondary 3A
180 Full Secondary 2A
150 2x Transformer rating 0.6A (220/80 x2)
130 2x Transformer rating 0.6A
110 2x Transformer rating 0.6A
90 2x Transformer rating 0.6A
70 2x Transformer rating 0.6A
40 Full Secondary 2A
20 Full Secondary 3A
So for an 80W transformer Fuse 1 can be 2 or 3A, & Fuse 2 a 1A.
See also my tech bul on "Maplin Mains Meter 2000MU-UK","Mains Power Protection"
& "Saveplug Motor Economiser".
Why don't U send an interesting bul?
73 De John, G8MNY @ GB7CIP
Read previous mail | Read next mail
| |