G8MNY  > TECH     22.04.24 00:01l 161 Lines 7198 Bytes #999 (0) @ WW
BID : 5938_GB7CIP
Read: GUEST
Subj: META HF Millennium 810H UPS
Path: IW8PGT<IZ3LSV<DB0ERF<DK0WUE<GB7CIP
Sent: 240421/2218Z @:GB7CIP.#32.GBR.EURO #:5938 [Caterham Surrey GBR] $:5938_GB
From: G8MNY@GB7CIP.#32.GBR.EURO
To  : TECH@WW

By G8MNY                                     (Updated Nov 12)
(8 Bit ASCII graphics use code page 437 or 850, Terminal Font)

This is some info I have found out on this Italian 100% Power Conversion UPS.
(Uninterruptable Power Supply)

The 1kW HF Millennium (810H), has 2x small paralleled 36V 7AH battery sets, so
I modified it for external batteries & front panel battery digital meter.

SYSTEM
It is not like the APC UPSs, as there is no big 50Hz mains transformer. The
META rectifies the mains to make ñ380V DC regulated @ 2A each, & inverts this
with HF class D amp into 50Hz 230V @ 5A sine wave. On battery mode it has a
DC-DC inverter from 36V @ 45A to the 380V DC. The THROUGH non inverting mode,
only comes on for overloads.

Although inverting at HF all the time I could not hear any QRM on 80m with my
external aerial.
                                                Bypass
                  ÚÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄ¿ _____ Mains 
        ÚÄÄÄÄÄÄ¿  ³ ÚÄÄÄÄÄÄÄÄ¿ ñ380V DC  ÚÄÄÄÄÄÄÄÄ¿  /      Out   
Mains >Ä´FilterÃÄÄÁÄ´AC-SM DCÃÄÄÂÄÄÄÄÄÂÄÄ´HF  50HzÃÄÙ
 In     ÀÄÄÄÄÄÄÙ    ÀÄÄÄÄÄÄÄÄÙ  ³     ³  ³Inverter³
                      ÚÄÄÄÄÄÄÄ¿ ³     ³  ÀÄÄÄÄÄÄÄÄÙ 
             36V   ÚÄÄ´ChargerÃÄÙ     ³
           BatteryÄ´  ÃÄÄÄÄÄÄÄÁÄÄÄÄÄ¿ ³
                   ÀÄÄ´DC-DC InveterÃÄÙ
                      ÀÄÄÄÄÄÄÄÄÄÄÄÄÄÙ
SPEC
  Input 186-264v full load, 110-265V 50% load.
  Output 230V ñ2% 50Hz Sine wave.
  Power 1kW max 4.35A resistive load. e.g. 700W max with PF 0.7 load.
  Freq Sync. will lock to mains if within tolerance e.g. ñ2Hz
  Bypass mode, only used on overloads.
  Efficiency 80% with 50-100% loads. (about 70W lost all the time!)

INTERNAL BATT TESTING
I did a 60W car headlamp test on each of the small 12v batteries, only 1 was
below 11V (10.9V) so I paralleled up all the batteries & put them on 13.8V
charge for a few hours to even up the charge. The 6 batteries are the standard
7AH 12v tagged type. I marked up the weak one for future reference in case it
stays weak. Currently the charge status reads 80%. (4 of the 5 LEDs on after
batt test.)

FAN FAULT
The 12V DC FAN was duff & alarms the UPS if plugged in. (brushless type draws
2A @ 12V & does not spin!). It has been running on a 27V supply, (duff reg?) so
I replace the fan with a quiet efficient 50V DC one I had rather than fault the
motherboard's fan regulator.

THE CASE
The case comes apart very strangely!
                     _________________________  Control Panel
                  6"/ /~~~~~~~~~~~~~~~~~~~~~~~~~\Ù
   Recessed Handle ³=³ Ú-----------------------¿ ³ Recessed Handle
             RS232>³#³ |                       | ³
                   ³ ³ |                       | ³
               Fan>³±³ |   Side Access Panels  | ³
                   ³ ³ | (5 small Screws each) | ³
                   ³ ³ |                       | ³17"
                   ³ ³ |                       | ³
                   ³ ³ |                       | ³
                   ³ ³ |                       | ³
 Mains in/out IECs ³#³ |                       | ³
Top U Cover Screws>³_³_|_______________________|_³<Top U Cover screws
                                  24"
After removing the steel side panels, the top steel U cover comes off with 3
plug leads.

Removing the centre PCB section steel frame with 4 small screws, leaves the
heavy bottom battery tray & mains filter compartment.

CONTROL PANEL
               ÚÄÄÄÄÄÄ BY PASS ÄÄÄ * Ä¿              * LEDs gives status
               ³ ÚÄÄÄ¿                ³ 
      MAINS * ÄÁÄ´~/=ÃÄ¿    ÚÄÄÄ¿     ÃÄÄ OUT     After batt Test No of LEDs
                 ÀÄÄÄÙ ÃÄÄÄÄ´=/~ÃÄ * ÄÙ           gives charge 20 40 60 80 100%
                 ÚÄÄÄ¿ ³    ÀÄÄÄÙ
    BATTERY * ÄÄÄ´=/=ÃÄÙ           * OVERLOAD
                 ÀÄÄÄÙ             * PROTECTION

         ( (1) )   ( (/) )
         On Off   Test & Alarm off

INSIDE               _________________________ Control Panel
                    /           ........pcb   \Ù
   Recessed Handle ) Ú-----------------------¿ ( Recessed Handle
             RS232>³ |³~~~~~~~~~~~~~~~~~~~~~³| ³
                   ³ |³                     ³| ³
               Fan>³ |³  Huge inverter PCB  ³| ³
                   ³ |³                     ³| ³
                   ³ |³                     ³| ³
                   ³ |³______ Mother_board__³| ³
                   ³ |       =============== | ³
                   ³ |~~~~~~³~~~~~~~~~~~~~~~~| ³
  IEC mains in/out ³ |filter³   Batteries    | ³
Top U Cover Screws>³_|______³________________|_³<Top U cover screws

SOFTWARE
There are no hardware options on the UPS, all are set using software.

EXTERNAL BATTERIES
As the use is for Broadcast Studio power, which needed long mains fails times,
I wired a 60A connector block on the back directy to the PCB where the small
batteries were connected. (bypassing the 2x 30A fuses). The External batteries
are 3x 110AH & has a 60A fuse in one of the battery jumper links, so all the
heavy wiring is protected. Theoretically this gives about 3 hrs backup at full
power! 

However the Battery "floats" near neutral & should not be earthed, as the mains
RCD can be tripped!
                     _________________________  Control Panel
                    /           ........pcb   \Ù
   Recessed Handle ) Ú-----------------------¿ ( Recessed Handle
             RS232>³ |³~~~~~~~~~~~~~~~~~~~~~³| ³
                   ³ |³                     ³| ³
               Fan>³ |³  Huge inverter PCB  ³| ³<Meter
                   ³ |³                     ³| ³
                   ³ |³                     ³| ³
                   ³ |³______ Mother_board__³| ³
                   ³ |       =============== | ³
     36V Connector>³:|~~~~~~³~~~~~~~~~//~~~~~| ³
  IEC mains in/out ³ |filter³========/cables | ³
Top U Cover Screws>³_|______³________________|_³<Top U cover screws

METERING
I also added a cheap large digital LED Meter UP5135 50V 100A to the front panel
so Volts & Current can be measured. The meter needed 24V @ 50mA & also a
current shunt. I used a 5W 330R & 24V zener to safely drop the Battery to 24V
voltage, over 24V the LEDs went off & the volts went even higher!

Battery+ >ÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÂÄÄ +>UPS
+36-42V   ÚÄÄÄÄÄÄÄÄÄÄÄÄÄÄ´
          ³             330
          ³    ÚÄ+24VÄÄÄÄ´ 5W       The current shunt only needed a
         +V ÚÄÄÁÄÄ¿      ³          few mV, so the voltge drop across
          ÀÄ´ LED ³     _³_         1ft of thick wire to the rear
          ÚÄ´ DMM Ã -V¿ /_\'24V     connector was more than enought
          -I ÄÄÂÄÄÙ   ³  ³  1W      I calibrated it (preset pot)
          ³    ÀÄ 0VÄÄÁÄÄ´          with a 10A load & DMM.
          ³              ³
          ³   Shunt      ³
Battery- >ÁÄÄÄÄÄÄÄÄÄÄÄÄÄÄÁÄÄ ->UPS
            Wire 0.001R

In use the meter reads 41.5V on charge @0.8A & down to 35V on discharge, after
3 hrs allowing a good estimates of the lifetime left to be made. At 500W mains
load, 17A is drawn 82% effiecent giving the backup liftime >4Hrs.


See my buls on "APC Smart 900 UPS", "Lead Acid Batteries", "Constant Voltage
Transformers", & "Mains Power Protector".


Why don't U send an interesting bul?

73 De John, G8MNY @ GB7CIP