|
G8MNY > TECH 22.04.24 10:01l 146 Lines 6895 Bytes #999 (0) @ WW
BID : 5989_GB7CIP
Read: GUEST
Subj: Small Alafontronica 500W UPS
Path: IW8PGT<IZ3LSV<DB0ERF<DK0WUE<GB7CIP
Sent: 240422/0642Z @:GB7CIP.#32.GBR.EURO #:5989 [Caterham Surrey GBR] $:5989_GB
From: G8MNY@GB7CIP.#32.GBR.EURO
To : TECH@WW
By G8MNY (Updated May 16)
(8 Bit ASCII graphics use code page 437 or 850, Terminal Font)
This small UPS, is "supposedly up to 500W" of power. It is a 50Hz pulse width
stepped square wave mains inverter all from small 7AH 12V battery when in
backup mode (e.g. 55A @ 11V ?)
FRONT INTENAL SIDE VIEW
ÚÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄ¿ heatsink ______
³ÚÄÄÄÄÄÄÄÄÄÄÄÄÄ¿³ ÜÜÜÜÜÜÜ reg Freq Volts ³RELAYS³ DATA
³³ùOn On[]³³ =======================================================PORT
³³ùBackup ³³ Ûßßßßßß __
³³ùCharge Off[]³³ Û ³~~~~~~~~~~~~~~~~³ ÚÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÁÄ¿
³ÀÄÄÄÄÄÄÄÄÄÄÄÄÄÙ³ Û ³ __________ ³ ³ ³
³ ³ Û ³ ³ ³ ³ ³ ³
³ ³ Û ³ ³ MAINS ³ ³ ³ ³ IEC
³ ³ Û ³ ³ TRANS- ³ ³ ³ 12V BATTERY ³ OUT
³ ³ ³ ³ FORMER ³ ³ ³ ³
³ ³ ³ ³ ³ ³ ³ ³
³ ³ ³ ³ ³ ³ ³ ³ FUSED
³ ³ ³ ÀÄÄÄÄÄÄÄÄÄÄÙ ³ ³ ³ IEC
³ ³ ³ ³ ³ batt fuse ³ IN
³ ³ ÀÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÙ ÀÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÙ
ÀÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÙ
DESCRIPTION
The transformer has tapped primary & 2 secondaries, one into a bridge & SCR for
charging. And the 2nd is the centre tapped inverter input winding. Two relays
control the mains side, one for mains tap & other for mains connection.
On power fail the mains relay releases & the 2 large Tab FET switching
transistors sandwiched in the heatsink, run at 50Hz giving the waveform below.
On mains return the 50Hz is 1st phase locked to the mains, before switching off
& connecting back to the mains. Another relay also changes the output tap on
backup mode.
OUTPUT WAVEFORM with load (ringy from transformer & filter)
+340V´ ÚÄÄÄ¿ Peak Voltage depends on Battery state & Load current!
+230V³ ³ ³ Pulse width varies to get 230V RMS?
³ ³ ³
0V ´ÄÄÙ ÀÄÄÄ¿ ÚÄ
³ ³ ³
-230V³ ³ ³
-340V´ ÀÄÄÄÙ
USES
Mainly for computerised kit, that might suffer file corruption, or even HDD
damage on some power fails. But note a "non on line" UPS can still be fooled by
bad "brown outs", where the mains voltage does not go straight out, but has a
few cycles close to the kit's PSU safe minimum voltage (e.g. drops to 150V for
1 second while someone is blowing a fuse & then out!) So kit PSU becomes
desperate for power & the UPS does not cut in, in time to stop the kit's PSU
giving illegal & corrupting voltages especially to CPUs, memories, & HDDs.
UNMANNED SITE MODIFICATIONS
As with most UPSs, this UPS is not suitable for an unmanned site. This is
because, when the battery is emptied/fails on a long discharge, not only does
the output fail, but the UPS then stays in OFF mode with no output power, even
when the mains is power restored!
Initially I designed 2 modifications to solve this...
1/ AUTO ON RE-START
I wanted the UPS to come back in automatically when the battery has recovered
after discharge. On scoping around the PCB, I found the ON button was just -12V
on a low current circuit, to the ON logic. There was also a pulsed +ve 18V
charging waveform feeding the charge LED via 1kê, that diminished to around 1V
when the battery was OK. So a little scratching of head I came up with this
circuit...
18V 100Hz 1N4148 1N4148
Charge ÄÄÂÄÄ220Ä´>ÃÄÂÄÄÄÂÄ´<ÃÄÄÄÂÄÄÄÄÄÄÄ>ON LOGIC
Pulses 1K ³+ ³ ³ ON
_³_ 10u=== 100k /button
Chargeð\_/ ³ ³ ³
ÄÄÄÁÄÄÄÄÄÄÄÄÄÄÁÄÄÄÁÄÄÄÄÄÄÄÁÄÄÄÄÄÄÄÄ -12v
When the pulses reduce, the 10u discharges through the 100K to level were the
12V ON electronics starts up, doing a self test & back on. Although with this
circuit the UPS does not come straight back on when the battery might be usable
after a UPS exhaustion event, but leaves the load on normal unprotected mains
via my 2/ mod. However it does come back automatically eventually & hopefully
with a usable well charged battery.
A label was added to warn of the modification & how to turn the unit off.
e.g. POWER OFF UNIT WITH MAINS ON & then disconnect mains input.
2/ OUTPUT FAIL BYSASS RELAY
By adding a small 5A double pole mains changeover relay (low current 30kê AC
winding) to the load side (on IEC socket), when the output fails, the relay
releases & the load is then connected direct the mains.
Mains L ÄÂÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄ¿nc
ÚÁÄÄÄÄ¿ \_____ L
³ ÃÄÄÄÄÄÄÄÄÄÄÂÄÄÄÄÄÄÄÙ
³ ³L 10k
³ UPS ³out- Ú´>ÃÄÁÄ´>ÿ LOAD
³ ³ ³ ³ WITH
³ ³put ÃÄÄRELAYÄÄ´ UPS
³ ³ ³ ³ FAIL
³ ³N À´>ÃÄÂÄ´>ÃÙ BYPASS
³ ÃÄÄÄÄÄÄÄÄÄÄÁÄÄÄÄÄÄÄ¿ _____
ÀÂÄÄÄÄÙ / N
Mains N ÄÁÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÄÙnc
But nothing is that simple, as my relay did not operate correctly & tended to
Buzz on UPS changeover. So I added a 4 diodes bridge & a series R of 10K (do
not use series cap on square wave mains!) This slowed down the action OK, from
10mS to <100mS.
Later after 50 days of trouble free use, a failure occured blowing the 3.12A
slow blow input mains fuse, I redesiged it with out this relay & also removed
the mains OFF relay & bridged that out with a wire link,
ÄÄÄÄÄÄÄÄÄÄÄÄÄÄ¿ In use this is bit better as there is less
Mains filter ³Rear arcing mains relays etc. But now there is a 2s
³of break on "power on", as the 50Hz Osc has to be
Missing ³PCB in mains sync before the C/O relay connects
Volts relay³ the mains (whether inverter is on or off!)
³
Removed ³ However this does not happen unless the
OFF relay ³PCB battery has flatened & then on a full
³Connector recharge, you get a clean short break.
Mains ON ³
C/O Relay ³ Anoying, but much prefured to blowing a fuse!
ÄÄÄÄÄÄÄÄÄÄÄÄÄÄÙ
SAFETY WARNING
The 12V DC side has a 32A fuse, this is a lot of current from a 7AH battery!
The fuse holder & battery connectons need to be kept clean & greased to ensure
good operation & no corrosive heating at these currents.
The UPS has the DC battery -ve is on the mains neutral, & not mains isolated!
I did all my testing with an isolated mains supply & a scope earthed to the
battery -ve.
Why don't U send an interesting bul?
73 De John, G8MNY @ GB7CIP
Read previous mail | Read next mail
| |